Issue No. 3
The purpose of the Quick-2 Mailing List is to provide up-to-date information about Quick-2 software, tutorials, and other related topics pertinent to the Federal Emergency Management Agency (FEMA) and the National Flood Insurance Program (NFIP).
This month we will re-visit the property we looked at last time. Our exercise this week will be to compute a Base Flood Elevation using actual field surveyed points and we'll do some sensitivity analyses. In doing doing this, we will use Quick-2 to do the following:
As you recall from last month, the grading design for this lot did not leave much room for error. Being a conscientious engineer, you decided to go out and survey the channel section, look at the error in the computed base flood discharge, and evaluate variations in n-values.
The results of the survey are given below:
Station(ft) |
Elevation(ft NGVD 29) |
|---|---|
0 |
247 |
200 |
245 |
300 | 242.5 |
600 | 242 (left bank) |
730 | 241 |
900 | 238 |
963 | 238 |
1010 | 239 |
1050 | 241 |
1200 | 242 (right bank |
1375 | 242.5 |
1525 | 243.5 |
1700 | 247 |
From last month's Listserv, we have the following data:
Base Flood Discharge: 3,800 cfs
Manning's n-value: 0.045
Downstream stream slope: 0.002 ft/ft
To determine the BFE using Quick-2 irregular channel, normal-depth method:
The results are displayed at the bottom of the screen in the "OUTPUT' section. The computed BFE (located in the WS Elev box) is 242.58 ft. The LAG for the property is 242.25 ft. Using the more detailed geometry we see that the property can not be removed from the SFHA.
To determine how sensitive the BFE is to n-values, simply click on the drop down menus for the n-value parameters, select a value from the list of possible coefficients, and click on 'Compute."
Try using values slightly above and below .045, like .04 or .05. Also it is a good idea to change the cross section ID each time you change parameters and compute a new water surface elevation. This way, you will be able to instantly recall the results of a previous calculation (using the cross section drop down box). It should be noted that even if you do not change the cross section number, the summary and detailed outputs under the View menu, will still record all of your computations.
Now, the USGS publication that gave us the regression equation to determine the base flood discharge reports that the error in the equation is 33%. This means the true discharge is somewhere between 2,546 cfs and 5,054 cfs. To test the sensitivity of the BFE to the discharge, simply click in the discharge box, enter a new discharge and click on 'Compute." Again, it is a good idea to change the cross section ID each time you change parameters and compute a new water surface elevation.
Quick-2 can automatically create a rating curve for the channel section. Click on 'View,' and select 'rating curve,' or click on the yellow rating-curve button in the upper right-hand side of the screen.
To view a cross section plot you can click on 'View,' and select 'Xsec Plot,' or click on the cross-section button in the upper right area of the screen.
While viewing the cross section plot, you can click on the 'Curve Now!' button and the rating curve will be plotted on the same graph as the cross section. Click on 'Print,' and you can show you're client why they should put at least another foot of fill on their site! (Hint: using the Rating Curve, or computing directly, see what water surface elevation is determined for a discharge of 5,000 cfs.)